True. If liquid goes into the compressor it would spoil. Therefore the refrigerant goes into the compressor as saturated vapour. That is why never set your thermostat to the lowest temp. if the load in space is low, e.g. rainy day or in the morning. So make sure the temperature at suction is not lower than approx -9.4 deg C.
Second thing: higher suction temperature back to compressor does not reduce compressor work but increase it. Very simple question: Why does the compressor needs to work harder when the heat inside a room is high? When the load in suction is high, that means the compressor has to give higher refrigerant flow rate in order to dissipate enough heat at the condensing side so that it can obtain 12~15 deg C at the evaporator coil.
COP of the system is Heat/Work (Q/W). The higher the Q, the lower the COP.![]()
Our evaporator now day come with electronic expansion valve where is can control the liquid refrigerant flow in to the system depend on heat load in the cabin. it will control the right quantity amount of liquid flow in to evaporator and make sure all the liquid fully vaporize at the evaporator outlet.
it depend on many condition, says your compressor,
SST (saturate suction temperature) is 4degC
SDT (saturated discharge temperature) is 50degC
delta T is about 46degC, meaning to say compressor need to compress from 4degC to 50degC to condenser coil to get heat rejection.
Lower the SST will push the compressor to work more.
if let say you have superheating about 1degC mean your SST will be 4+1degC, hence delta T 50-(4+1)=45degC
It reduce the compression ratio between SDT and SST.
. It's the whole car going for RM29k nego!